Skip to main content

User Guide

Focus Chart

Visualization modes

As soon as a tag or attribute is added and active, it's visualized on the focus chart. The focus chart can present your data as a:

  • Stacked trend plot

  • Trend plot

  • Scatter plot

The stacked trend plot is the default visualization mode. The mode can be changed by clicking the focus chart visualization mode button underneath the chart.

2026_R1_0_focuschart_01_VizualizationModes.png

In stacked trend plot mode, each tag or attribute receives an individual swim lane on the chart to visualize its time series data. 

As displayed on the image above, you can see three swim lanes. By default, each of these swim lanes represent one tag or attribute. On the left of each row, the y-axis is located. By default, the y-axis of each tag is set to the auto scale setting which makes sure all data is visible. The auto scale updates when needed.

The scale setting can be changed for each tag individually (auto or manual scale) and will be remembered for future sessions.  Underneath the swim lanes an x-axis is shown, which represents the date and time range of the visualized focus chart.

A second visualization option is called Trend.

2026_R1_0_focuschart_02_RegularChart.png

All tags and attributes are shown in one large swim lane with labels set above the chart, which is the main difference compared to the stacked trend plot.

To avoid clutter of the chart, the regular trend chart offers the ability to hide (or visualize) a y-axis for the second and following tags or attributes on the chart. This is done by clicking the label of that tag in the focus chart.

2026_R1_0_focuschart_zoomed_01_AdditionalAxis.png

The third visualization option is the scatter plot. The (multi) scatter mode highlights correlations between the different visualized tags for the selected time period. More details about the scatter plot can be found on this link.

Per chart there are different settings you can modify to fine-tune the chart to your liking. The settings are found at the top right of the focus chart behind the blue settings button.

2026_R1_0_focuschart_03_RegularPlot_settings.png
2026_R1_0_focuschart_04_StackedPlot_settings.png

For the 'Trend' and 'Stacked trend' chart the following settings are available.

  • Context items: When enabling the "Context items" option, the context items associated with the period you have visualized will appear on the chart. This option is enabled by default for both time series visualization modes.

    Note

    Many context items will impact the performance of the chart.

  • Trendline filling: By checking the 'Trendline filling' option, the area under the curve of each tag and attribute will be filled with a shaded color. This option is enabled by default for the Trend charts.

  • Gridlines: Selecting this option places gridlines onto the chart, making it easier to read the values. This option is disabled by default for both time series visualization modes.

  • Chart label: This dropdown allows you to specify how tags or attributes will be indicated on the focus chart (Name, Alias or description). The alias is selected by default. Tag or attribute names will be used as fallback in case there is no chart alias or description available. A custom chart alias can be set in the tag details. See this article for more information.View tags details & customize tag visualization

  • Collapsed filters: Enables collapsed view mode, which hides filtered regions and scales the remaining visible data to fill the entire focus chart. This mode is only available for the base layer and is disabled by default. 

The stacked trend visualization offers 1 additional setting, called Single-line labels. By default, the label of a tag or attribute is positioned in its respective swim lane. By enabling this option, all labels are positioned at the top of the focus chart, similar to the regular trend plot. This is particularly useful when you want to visualize a lot of tags and optimize the screen estate.

Note

The settings of the different visualization modes are saved separately for your user, which means you can have one setting enabled for one mode while that same setting is disabled for the second mode. The options will be saved and reused in your next session. Collapsed filters, will always be disabled when starting a new session/view. 

Note

All chart settings are saved inside a view. Meaning, when a colleague opens one of your shared views, your chart settings will be enabled for that view.

Reorganizing tags, attributes

In both trend modes you can reorganize the tag labels on the chart by grab and drop to another location. In the trend plot you move a label next to another, while in the stacked trend plot you move the labels in between different swim lanes.

By doing this the order of tags and attributes will be changed on the plot as well as in the Tags & Attribute list.

Creating groups is also possible. You can do this by dropping a label on top of another label. Once a group is created, the scale setting of the first tag in the group is used for the whole group. Group scale settings can also be adjusted. Click the group in the Tags & Attributes list to do this.

Note

For more information about grouping please check the following link.View tags details & customize tag visualization

Creating data scooters

Data scooters are boxes on the focus chart that contain the values of all the visible tags and attributes at a specific time on the base layer. For analog tags, values are linearly interpolated. For discrete, string and digital tags, the value of the last recorded point is displayed. You can create an unlimited number of data scooters to compare your values of the base period at every moment in time.

Adding data scooters is done by double clicking anywhere on the focus chart (Trend and Stacked trend plot). Each data scooter can be grabbed and dragged to another position on the focus chart as desired. A single data scooter can be removed in two ways. Double click anywhere on an existing data scooter or click on the cross button in the top right corner of the data scooter.

Note

When data scooters are used on large zoomed out periods with rapidly varying data, the accuracy of the values displayed on the data scooters are limited. Best results are obtained by zooming in on the desired period.

When a data scooter is created, you will see the three vertical dots button. Clicking this button reveals the options for the data scooter:

  • Add context item - Is a data scooter showing the start of something that is going wrong? Mark it with a context item. Clicking the data scooter's 'Add context item' button will start the creation of a context item.

    The advantage of creating a context item in this way is that the start date and time are automatically filled out for the context item you are trying to create, after entering a context item type. An end date and time can be set after the creation of the context item.

    More information about the creation of context items can be found here.

  • Remove all - A single data scooter can be removed in two ways. Double click anywhere on an existing data scooter or click on the cross button in the top right corner of the data scooter.

    It is also possible to remove all data scooters at once. To do this, click on the three vertical dots button in any of the available data scooters, which reveals the data scooters option list. Click the 'Remove all' option to remove all data scooters.

    2026_R1_0_focuschart_zoomed_01_DataScooterOptions.png

Focus chart selection

You can create a selection on the focus chart by dragging and dropping your mouse over the focus chart. While doing this you can immediately see a grey box appear on the top left corner of the length of period you are creating.

Once completed, you can see a highlighted period, and a popup that provides you with actions that can be applied to the highlighted period.

2026_R1_0_focuschart_zoomed_02_FocusChartSelection.png

You have the following options:

  • Zoom: This option will zoom into the selection on the chart you have created.

  • Add context item: Did something happen in the selected period? Mark it with a context item. Clicking this option will start the create context item flow.

    The big advantage of creating a context item in this way is that the start / end date and time are automatically filled out for the context item you are trying to create, after you enter a context item type.

    More information about the creation of context items can be found here.

  • Weight: Increase the density of the tags and attributes in that period. Weights are used in similarity searches, to increase the importance of that selected period.

    More information about weights and similarity search can be found here.

  • Manual filter: With this filter option, you can exclude the selected period (or include it again). Filtering out periods removes them, ensuring that they are not used in any subsequent analyses in TrendHub (e. g., statistics / compare layer table, searches, etc.)

    Filtered out period settings can be saved, meaning you can use them in later sessions.

    More information about filters can be found here.

When you have multiple filtered periods in your focus chart, collapsed filters mode allows you to view your data without the visual interruption of filtered-out regions. This mode hides all filtered periods and scales the remaining visible data to fill the entire focus chart, making it easier to spot patterns and trends in your active data.

Enabling Collapsed Filters

There are two ways to enable/disable collapsed filters:

  1. From the filter menu: Click on any filter indicator on the focus chart and select "Collapse all " / “Expand all” from the popup menu.

  2. From chart settings: Enable/disable the "Collapsed filters" option in the focus chart settings (gear icon at the top right).

When collapsed filters mode is enabled, collapsed indicators (parallel lines) appear at the locations where filtered periods have been hidden. When auto-scaling is enabled for the tags, the Y-axes auto-scales based only on visible (non-filtered) data, ensuring optimal visualization.

2026_R1_0_focuschart_zoomed_03_BeforeCollapsing.png
2026_R1_0_focuschart_zoomed_04_Afterollapsing.png

Behavior and Limitations

Base layer only: Collapsed filters mode works only on the base layer. Enabling this mode hides all visible layers. When you use features that use all data (similarity search, predictive mode, fingerprints) or add layers, collapsed mode disables automatically. A notification informs you of this.

Zooming restrictions: Mouse scroll zooming is disabled in collapsed filters mode

Compare layer: The compare layer functionality is disabled when collapsed filters mode is active. 

Live mode: Live mode continues to work normally when collapsed filters mode is enabled. New data points are added to the chart in real-time, respecting the collapsed view.

Navigation

TrendMiner's easy to use time navigation will help you move quickly through all your data that is being visualized, to find trends that help you define a problem or to confirm a hypothesis.

Data is visualized on the Focus chart and the Context chart.  The Context chart sets the scene and defines the data on which specific searches and filters will be applied. The Focus chart represents the biggest part of the application and shows the time series data for the period of interest. Both levels can be used to navigate in time.

2026_R1_0_focuschart_05_TimeChartDivision.png

The focus chart itself offers various controls for time navigation.

Chart zooming (in and out) can be done in scroll fashion with your mouse or touchpad.

You can also zoom in on the chart when a selection is created on the focus plot. This is done by a click and drag action on the focus chart, creating a greyed selection. By doing this you are highlighting your interest in the period. When the area is selected, a selection menu appears including a zoom option.

You can click and drag the time axis to move through time or expand the visible period.

How panning behaves depends on the state of the lock in the Focus Chart controls:

  • Locked — the visible period stays the same length and shifts in time.

    • Drag the time axis to the right to view older data.

    • Drag the time axis to the left to view more recent data.

  • Unlocked — the visible period grows, adding more data on one side.

    • Drag the time axis to the right to add older data. The end date stays fixed.

    • Drag the time axis to the left to add more recent data. The start date stays fixed.

Note

Note: The default value of the lock button is set to unlocked.

Below the focus chart there are options which give you the ability to move through the time on the focus plot.

2026_R1_0_focuschart_06_FocusChartControls.png

The shift buttons (left and right arrow buttons) will shift the focus chart into their respective directions. The response here depends on the state of the lock button, mentioned earlier.

When the button is unlocked, both buttons will add 20% of the current window size to the period. When the lock button is locked, the buttons will move the chart to the left or right, by 20%.

Next to the shift buttons on the left and right, you will find the date and time pickers. Use these buttons to select the start and end time of the focus chart.

To the left of the focus chart visualization button, sits the time span selection option. By selecting the time span picker, you open an option to apply preset time frames to the focus chart, enabling a quick and effortless way to frame the time span you wish to analyze.

The start time is updated when using this option, but the end date remains the same.

The following time frames are included: 1 - 2 - 8 hour(s), 1 - 7 - 30 day(s) or the possibility to enter specific time periods.

With the custom time period you can select the exact period you wish to see displayed on the focus plot. To input a period simply use y for year, M for month, w for week, d for day, h for hour, m for minute and s for second.

E.g.: for a period of 1 week, 2 hours, 2 minutes, and 10 seconds, simply input the following:

  • 1w 2h 2m 10s, then press enter.

  • Once you press enter, the focus chart expands or contracts to the period you requested.

The lock button itself is located to the right of the time span selection button.

The final chart control button, is the undo time navigation button, located to the right of the lock button. This option is by default disabled but can restore any functional change to your current view regarding the previous state of the date and time settings, thereby undoing any time navigation action.

Note

When you load a new view, enable predictive mode, or enable a live mode view, the undo time navigation button is reset.

The context chart shows an overview of the relevant data to examine (applicable on searches and filters). Below the chart you will find tools that can help you set your context chart, and also help you understand the link between the context and focus chart.

2026_R1_0_focuschart_07_ContextIndicator.png

The context period is the period that is visualized in the context chart and is the period that is used when performing searches or activating filters in TrendHub.

There are multiple ways to change the context period.

Note

Each update with these buttons immediately adjusts the context period and chart. Any changes made can be reverted with the "undo time navigation" button.

Note

The default value of the context period, when logging in to TrendHub, is set to 3 months.

  1. Beneath the context chart, you will see options that indicate a period of time. The first group of options are predefined periods. Clicking these buttons zooms the context chart into one of the following periods:

    • One day (1D), now moment - 1 day

    • One week (1W), now moment - 7 days

    • One month (1M), now moment - 1 month

    • Three months (3M), now moment - 3 months

    • Six months (6M), now moment - 6 months

    • One Year (1Y), now moment - 1 year

    • All data (ALL), Start of index horizon to now moment

    Note

    The months / year durations mentioned are effectively a month or a year. E.g.: 3 months --> from 2nd of January 2022 08:30:00 to 2nd of April 2022 08:30:00.

  2. On the right of these predefined buttons, a "Custom" button, allows the setting of a customized context period.

    • With the first option "Context period range", you can enter a custom period which behaves the same as the predefined buttons. Meaning, you can set the desired last 'custom range' (E.g.: 5d 8h 50m 42s) which results in the now moment - entered value.

    • The second option "Custom context period" lets you define the start AND end date, and time for the context period.

    Note

    When the custom button is set, the entered value will be displayed in a tooltip when hovering on the button.

    2026_R1_0_focuschart_08_Context_customTimeWindow.png
  3. Another way to update the context period is to use the button  "Zoom context chart to selected area" which is located to the right of the "custom" button. Clicking this button will zoom your context chart into the period you have visualized on the focus chart.

  4. As a final option you can adjust the context chart by dragging the time axis of the context chart. Similar to the focus plot, where you can increase or move the time axis depending on the state of the lock.

The context chart provides a rough indication of the evolution of the time series data in the selected context period. The period which is visualized on the focus chart is indicated on the context chart.

The following actions can be used to modify the focus chart:

  • Selecting a region on the context chart.

  • Adjusting the selected region by using the edges.

  • Moving the selected period by moving the white box underneath.

  • Selecting the complete context chart by clicking on the outside of the selected region.

Note

For easy navigation to a period of interest, it is often best to first select a longer period by using the context chart, then work a more accurate selection on the focus chart.

Exporting data